I checked all, and seems to be OK.
We have connected the Push to the L3 and N. Can that cause the funny readings?
I attach photos. We thoroughly checked that CT1 and L1 are the same, as CT2 and L2, CT3 and L3. The arrows are in the load direction. There are no generators on the internal grid.
Search found 2 matches
- Thu Aug 13, 2015 9:38 pm
- Forum: Electric Meters
- Topic: unbalanced reverse
- Replies: 3
- Views: 8657
- Mon Jul 27, 2015 8:26 am
- Forum: Electric Meters
- Topic: unbalanced reverse
- Replies: 3
- Views: 8657
unbalanced reverse
I just installed 3 phase v3 EKM with 800A CTs. Data coming in just fine. But I have trouble understanding what is going on. It is installed in a hotel. There are 3 phases coming in at 120v to neutral each, but all the loads are 120v or 208/240v, there are no 3phase loads. And the distribution is thr...