Search found 3 matches
- Wed Feb 27, 2013 6:23 am
- Forum: Electric Meters
- Topic: Paralleling CTs
- Replies: 5
- Views: 10694
Re: Paralleling CTs
I checked and I have the V3 meter so I am still concerned about the fact that L2 power is not moving at all and L1 power is moving along. I don't think there is a total power screen showing. Please advise.
- Sat Feb 16, 2013 1:59 pm
- Forum: Electric Meters
- Topic: Paralleling CTs
- Replies: 5
- Views: 10694
Re: Paralleling CTs
Thanks for your response. I rechecked my wiring and found that I had wired L1 voltage with L2 CTs and visa versa. I corrected this, checked it a few days later which raised another question I forget to ask earlier. Prior to correcting the wiring I had kWh readings of the same magnitude on L1 (544 kw...
- Sun Feb 03, 2013 1:58 pm
- Forum: Electric Meters
- Topic: Paralleling CTs
- Replies: 5
- Views: 10694
Paralleling CTs
I recently installed an EKM meter on a 208 volt (2 hots one neutral) and had to use two CTs for each side of the panel as I could not reroute all of the lines to one side of the panel. Basically L1 has two CTs and L2 has two CTs. Both were wired in parallel and I made sure all of the lines going thr...