Search found 23 matches

by Garry
Fri Mar 27, 2015 7:03 pm
Forum: Water Meters
Topic: Dashboard setup
Replies: 6
Views: 34828

Re: Dashboard setup

Used setting u suggested but had to set Pulse Value at 0.0001 because Pulse Input Ratio is set at 1000. How can you change the Pulse Input Ratio? I saw in other comments that it is set in the software; I guess I really don't need to change it since I just adjusted the pulse value.
by Garry
Wed Mar 25, 2015 5:21 pm
Forum: General Discussions
Topic: Event Manager
Replies: 2
Views: 27005

Event Manager

I can see all items in Event Manager, but can't select anything; all items are "greyed" What don't I have turned on?
by Garry
Wed Mar 25, 2015 5:15 pm
Forum: Water Meters
Topic: Dashboard setup
Replies: 6
Views: 34828

Dashboard setup

Have a Pulse v4 trying to setup Dashboard to monitor flows from 2 meters connected to it. Would like to monitor flows down to 1 gpm. With 3/4" meter sending pulse for .75 gal, what should pulse value be set at? Pulse Input Ratio is factory set at 1000:1 so I have set Pulse Value at 0.001. On Da...