Reading pulse signals to external controller
Posted: Thu Aug 04, 2022 9:51 pm
My EKM 3/4" water meter has the two pulse-output wires and it is giving accurate pulses wired to my Omicron H7EC counter. Rather than installing a $200 Hunter Flow-Sync wired to my Hunter I-Core commercial irrigation controller, I'd like to use the pulse output directly from the EKM water meter.
There is a "K-Factor" and an "Offset" setting that is needed to configure a non-Hunter flow sensor. The Hunter manual states this is specified by the manufacturer of the flow sensor. As I understand it, the K-Factor is defined as the number of pulses generated per unit of volume. The EKM 3/4 " meter specifies 1 pulse = 0.1 cubic feet or 0.75 gal. That would be the K-Factor. However, I'm not sure what the Offset would mean, other than the accuracy rate or min/max flow rate. Any clues on what this would mean, of if it is even important at all.
There is a "K-Factor" and an "Offset" setting that is needed to configure a non-Hunter flow sensor. The Hunter manual states this is specified by the manufacturer of the flow sensor. As I understand it, the K-Factor is defined as the number of pulses generated per unit of volume. The EKM 3/4 " meter specifies 1 pulse = 0.1 cubic feet or 0.75 gal. That would be the K-Factor. However, I'm not sure what the Offset would mean, other than the accuracy rate or min/max flow rate. Any clues on what this would mean, of if it is even important at all.