I don't have an RS485 adapter so I can access the settings on my new v.4 Omnimeter, which I'm using to monitor an EKM gas pulse meter. I can't get the meter to register the pulses from the gas meter and I'm assuming it's because the ratio setting isn't 1:1 like I expected. I figured this out based on what I read in this thread.
http://forum.ekmmetering.com/viewtopic.php?f=10&t=3323
Until I get an RS485 adapter to check the settings, what is the default ratio the v.4 Omnimeter is set to on the pulse reading inputs?
default pulse counting ratio on v.4 Omnimeter
-
- Posts: 3
- Joined: Sun Aug 10, 2014 12:07 pm
-
- Posts: 56
- Joined: Fri Dec 16, 2011 10:42 pm
- Location: Victoria, Australia
Re: default pulse counting ratio on v.4 Omnimeter
Pulse Ratio for 1, 2 & 3 are each set to 1000:1 by default.