meter reading when 2 CT's are connected
coolcatiger
Post by coolcatiger »
Hi
I have EKM meter installed with two CT's to measure solar production from 2 inverters. My data shows
P = 2582
L1_P = 18
L2_P = 2562
L3_P = 0 (makes sense because nothing is connected here)
L1_V = 0
L2_V = 123
L3_V = 0
L1_P only shows 18 , L1 is connected to inverter with the same number of panels as L2 which shows 2582.
Do you think L1_P is not reading correctly.
When I connected another measuring device (currentcost) to same lines I see reading from both lines.
Please advice how EKM is supposed to read two CT's
Re: meter reading when 2 CT's are connected
Hello coolcatiger,
It looks like your meter is not properly sensing voltage on Line 1. Please check your Line 1 voltage reference wire and it's connection to port 7 of your Omnimeter. If it looks good, use a ammeter to measure the AC voltage from port 7 to port 10. Insert your ammeter probes into the head of the phillips screws in the terminal blocks.
L1_P is for watts on Line 1.
L1_V is for volts on Line 1.
Watts = volts x amps x power factor.
If you do not have volts registering correctly on line 1, the meter will not be able to calculate watts or kilowatt hours correctly.