EKM - 25EDS - N v.2 - Correct wiring for UK Single Phase 240
stelip
Post by stelip »
I want to check that I have wired my meter up correctly for the UK 240v single phase supply.
Here is what I have
Single CT connected into the terminals 1/2 Monitoring the Live (L)
NO CT connected to terminals 3/4
Live connected to 7
Neutral connected to 8
The meter shows the correct voltage ~245-250
The amps looks correct.
It seems to be working correctly, Except that it dosn't appear to be tracking the utility meter.
Best regards
Steve
Re: EKM - 25EDS - N v.2 - Correct wiring for UK Single Phase
Hello Steve,
I assume that you have the old EKM-25EDSP-N (considered a North American meter, though it can be fudged to work with your power) is this correct? Or do you have the EKM-23EDS (this meter is for foreign 2-wire systems)?
stelip
Post by stelip »
Its the EKM-25EDSP-N
(Wanted this one as two of the pulse counts are connected to east/west solar arrays AC100 meters)
Have I got the fudge correct the N/L into the 7/8 pins?
Steve,
The 25EDSP-N is designed as a US power meter (we have replaced this meter with the Universal Omnimeter Pulse v.4 that will work with any system in the world)
In order to have the 25EDSP-N work on your UK 230 volt 2-wire system, you will need to use 1 CT (it sounds like you have your meter connected properly) and you will need to DOUBLE the kWh value the meter reports.
Let us know if this helps.
stelip
Post by stelip »
Doubling the value looks much closer than before. I will run a few tests over the next few days to let you know how it goes. Presumably I also need to double the reverse KWh.
Many thanks.