Subpanel
t84a
Subpanel
Post by t84a »
I built an addition that houses a subpanel for the electric for the addition as well as our hot tub. I would like to install a submeter to monitor the kw used by the subpanel. It looks like a typical install (see pic). So my parts list is:
EKM-OmniMeter II UL v.3 – Universal Smart Meter, Single Phase or 3-Phase, 120 to 240V, 50/60Hz, up to 5000 Amps
2x Split-core CT, 200A, 200A:26.6mA, 13mm (0.51") Hole Diameter, SCT-013-200
Indoor Enclosure Kit EKM-IENC
I watched the video and it seems very straightforward. Do I have the right stuff? Thanks
Re: Subpanel
Hello t84a! Welcome to our forums!
Thanks for the photo and the clear description of what you are looking to purchase!
Your photo does look like a typical 120/240 volt 3-wire US residential system. You have 2 hot wires (in this case both black) coming in at the top of your sub-panel. If you measured the voltage between these 2 wires you would get roughly 240 volts. If you measured the voltage from either of the hot wires to a neutral wire you would get roughly 120 volts. Your install will be very similar to the video you referenced:
https://www.youtube.com/watch?v=nvTTFxy_yQw
Here is additional information about 120/240 volt 3-wire systems:
https://help.ekmmetering.com/support/so ... v-metering
The items you are intending to buy look correct. I would double/triple check that the wires you want to install the CTs on are under 13mm in diameter (under 1/2"). Buying CTs that are too small to fit the wires you want to measure is one of the more common mistakes in ordering.
I would also consider buying 2 of the 1 amp Inline Fuse Holders. I would install these close to the voltage reference in the sub-panel. These will protect the voltage reference wires that feed your submeter.
If you are planning on submetering Water or Gas in the future I would consider the Omnimeter Pulse v.4, otherwise the Omnimeter II v.3 UL will work well for your needs.
With the Omnimeter II v.3 UL connected as a read off the face (not connected to a computer) you will be able to keep track of how much energy is moving through this subpanel over time. You have the option to add connectivity to a computer or to the internet at a later date.
Hope this helps. Let us know if you have any questions.
t84a
Re: Subpanel
Post by t84a »
Thanks. Just the info I was looking for. Can I use a GFCI breaker as a reference? I'll report back on my progress.
Re: Subpanel
Yes, a GFCI breaker should be fine.
