Specifications of CT Output
edozien
Post by edozien »
I would like to use EKM CTs with my own meters. I understood from the documentation that the output of the CT is a current that is proportional to the current in the wire passing through the core, with a maximum of 26.6mA. However when I monitor the raw output (white and black wires) with the ammeter of my meter it is consistently 0. I then tried to monitor the voltage accross the white and black wires. I get a measurement starting at 0.100006103515625 V but increasing in a way that does not appear to be proportional to the current in the wire passing through the core.
Do you have an API/specification for your current meters that can guide me? Or a circuit of how to make the voltage across the leads proportional to the current passing through the core?
Edozien
Re: Specifications of CT Output
Hello Edozien,
Make sure you are measuring the milliamp output of the CTs as AC (alternating current).
If you are using a 200 amp CTs and you pass 200 amps through it, the CT will output 26.6mA AC.
I would suspect that you would also see a much higher voltage (if your CT wires are open circuit). It is not going to be proportional to the current on the primary wire however.
I would look for voltage output CTs (3.33 volts is common) if you would prefer to measure the voltage. Voltage output CTs are designed differently than our CTs.