Specifications of CT Output

Posted: Sun Apr 28, 2013 2:08 am
by edozien
I would like to use EKM CTs with my own meters. I understood from the documentation that the output of the CT is a current that is proportional to the current in the wire passing through the core, with a maximum of 26.6mA. However when I monitor the raw output (white and black wires) with the ammeter of my meter it is consistently 0. I then tried to monitor the voltage accross the white and black wires. I get a measurement starting at 0.100006103515625 V but increasing in a way that does not appear to be proportional to the current in the wire passing through the core.

Do you have an API/specification for your current meters that can guide me? Or a circuit of how to make the voltage across the leads proportional to the current passing through the core?

Edozien

Re: Specifications of CT Output

Posted: Mon Apr 29, 2013 10:43 am
by Jameson
Hello Edozien,

Make sure you are measuring the milliamp output of the CTs as AC (alternating current).

If you are using a 200 amp CTs and you pass 200 amps through it, the CT will output 26.6mA AC.

I would suspect that you would also see a much higher voltage (if your CT wires are open circuit). It is not going to be proportional to the current on the primary wire however.

I would look for voltage output CTs (3.33 volts is common) if you would prefer to measure the voltage. Voltage output CTs are designed differently than our CTs.

Thanks,