unbalanced reverse
Posted: Mon Jul 27, 2015 8:26 am
I just installed 3 phase v3 EKM with 800A CTs. Data coming in just fine. But I have trouble understanding what is going on.
It is installed in a hotel. There are 3 phases coming in at 120v to neutral each, but all the loads are 120v or 208/240v, there are no 3phase loads. And the distribution is through 2 120/208v panels, so the loads are not balanced over the 3 phases at all.
On one of the phases, I have a cos Phi of 0.4C. And thre is forward and reverse kWh. but there is no generator present.
Is this because of the imbalanced loads? We have checked the arrows on the CTs, they are all in the same direction. We did not configure anything at all on the meter or push box, and since it is a remote site, we can´t check anything there now. We should have configured the 800A CTs, but the meter thinks they are 200A CTs, so we just have to multiply the kWh by 4 right?
I attach the measurements so far.
Why can´t I attach a CSV, TXT, XLSX, not even pdf????
here´s the link to the file in my public dropbox folder
https://dl.dropboxusercontent.com/u/131 ... ComoNO.csv
Any help with explaining what is going on would be apreciated.