EKM-Omnimeter RS-485 Data
Post by Jameson » Wed Nov 09, 2011 9:57 am
I wanted to start a discussion about how to parse the data coming from the EKM-Omnimeter.
Here is a link to the string parsing for our EKM Omnimeter: http://documents.ekmmetering.com/Meter_ ... ter_v3.pdf
This is a simple request response string that returns most of the data that is stored inside of the meter. If you use our free software and a serial sniffer software it will simplify your job to be able to "see" the request and response. The last 2 bytes are a CRC-16 checksum.
30 represents a 0, 31 represents a 1, 32 represents a 2, etc
Seth
Re: EKM-Omnimeter RS-485 Data
Post by Seth » Mon Dec 05, 2011 1:50 pm
The link provided above is no longer accessible. Use this:
TimAlls
Post by TimAlls » Sat May 12, 2012 1:42 pm
I am a boatbuilder and a Labview Programmer....I am looking at your metering system and considering using it in our product line since the meter I was using (ECM6300) is no longer available.
Please explain the structure of the data request....The return looks pretty simple....
Is the return data length always the same?
How is the CRC calculated?
When I am done with my code I can post it for free downloading.....I will be doing more a more graphical display with real time trend charts, history, etc..
Tim Alls
AllSeas Yachts
allseasyachts.com
Post by Jameson » Mon May 14, 2012 1:15 pm
Hi Tim,
This sounds really good! We are looking forward to seeing what you come up with. Labview looks like an interesting tool to use for displaying meter data. We are always interested in new ways to read the meters and are happy to hear you are willing to share the software when you are done. Thanks!
Meter Request:
The meter request is fairly simple. Here is the sample from the pdf: 2f 3f 30 30 30 30 30 30 30 31 30 30 31 35 21 0d 0a This is for meter # 10015
Here is an additional example for meter # 12345: 2f 3f 30 30 30 30 30 30 30 31 32 33 34 35 21 0d 0a
The rest of the data request does not change (there is no checksum for the request). Remember that the meter serial settings for the Omnimeter are 9600 baud, 7 data bits, even parity, 1 stop bit, and no flow control.
Return Data: Yes the return data length is always the same (255 bytes).
CRC Calculation (this is a bit wordy, so if you have any questions, please let us know): The CRC is a CRC-16 checksum. It is good if you can use this to determine if the data is good (but not essential) It gets a little challenging because our meters communicate with 7 bits rather than 8. The last 2 bytes in the response string are the CRC-16.
In this example string from an OmniMeter:
2 10 17 13 30 30 30 30 30 30 30 30 30 31 32 33 30 30 30 30 35 33 35 38 30 30 30 30 33 31 39 36 30 30 30 30 32 31 36 32 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 35 30 30 30 30 30 30 30 35 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 31 32 31 39 31 32 32 38 31 32 31 38 30 30 33 35 30 30 30 30 35 30 30 30 33 35 30 30 30 30 34 31 35 30 30 30 30 30 38 30 30 30 30 30 34 31 35 30 30 30 30 39 31 30 30 20 31 30 30 4C 30 39 38 43 30 39 31 30 30 34 37 32 35 30 30 31 31 30 30 38 32 36 30 35 30 37 31 37 33 38 35 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 30 21 D A 3 2B 6E
The checksum is the last 2 bytes, and is calculated on the second through the third from last bytes (H10 through H03, including the H10 and the H03). Because it is CRC-16, and because we use 7-bit bytes, we only have 16K possibilities with 2 bytes, as opposed to 64K possibilities using 8-bit bytes.
Here's one explanation:
1. An Initial 16-Bit CRC seems to have been calculated with the Polynomial 0xA001 or 0x5001. The routine for the CRC calculation is very standard. The way I figured these out is by a test program trying every polynomial between 0x0000 and 0xFFFF.
2. Then, depending on whether your processor is Big Endian, or Little Endian, the Bytes in the CRC16 need to be swapped (In my case, since Little Endian, the swap was required.)
3. Finally, Convert this 16-Bit CRC to a 14-Bit CRC by performing the following (and the following only) masking :
CRC &= 0x7F7F; -------> Thus, masking out the 7th, and 15th bits.
Here is our CRC code... This is a standard lookup table implementation with the standard CRC16 polynomial, the differences in computation are in the code, dealing with the initial value, endianness, and 7-bit encoding.
static const uint16_t const ekmCrcLut[256] = {
0x0000, 0xc0c1, 0xc181, 0x0140, 0xc301, 0x03c0, 0x0280, 0xc241,
0xc601, 0x06c0, 0x0780, 0xc741, 0x0500, 0xc5c1, 0xc481, 0x0440,
0xcc01, 0x0cc0, 0x0d80, 0xcd41, 0x0f00, 0xcfc1, 0xce81, 0x0e40,
0x0a00, 0xcac1, 0xcb81, 0x0b40, 0xc901, 0x09c0, 0x0880, 0xc841,
0xd801, 0x18c0, 0x1980, 0xd941, 0x1b00, 0xdbc1, 0xda81, 0x1a40,
0x1e00, 0xdec1, 0xdf81, 0x1f40, 0xdd01, 0x1dc0, 0x1c80, 0xdc41,
0x1400, 0xd4c1, 0xd581, 0x1540, 0xd701, 0x17c0, 0x1680, 0xd641,
0xd201, 0x12c0, 0x1380, 0xd341, 0x1100, 0xd1c1, 0xd081, 0x1040,
0xf001, 0x30c0, 0x3180, 0xf141, 0x3300, 0xf3c1, 0xf281, 0x3240,
0x3600, 0xf6c1, 0xf781, 0x3740, 0xf501, 0x35c0, 0x3480, 0xf441,
0x3c00, 0xfcc1, 0xfd81, 0x3d40, 0xff01, 0x3fc0, 0x3e80, 0xfe41,
0xfa01, 0x3ac0, 0x3b80, 0xfb41, 0x3900, 0xf9c1, 0xf881, 0x3840,
0x2800, 0xe8c1, 0xe981, 0x2940, 0xeb01, 0x2bc0, 0x2a80, 0xea41,
0xee01, 0x2ec0, 0x2f80, 0xef41, 0x2d00, 0xedc1, 0xec81, 0x2c40,
0xe401, 0x24c0, 0x2580, 0xe541, 0x2700, 0xe7c1, 0xe681, 0x2640,
0x2200, 0xe2c1, 0xe381, 0x2340, 0xe101, 0x21c0, 0x2080, 0xe041,
0xa001, 0x60c0, 0x6180, 0xa141, 0x6300, 0xa3c1, 0xa281, 0x6240,
0x6600, 0xa6c1, 0xa781, 0x6740, 0xa501, 0x65c0, 0x6480, 0xa441,
0x6c00, 0xacc1, 0xad81, 0x6d40, 0xaf01, 0x6fc0, 0x6e80, 0xae41,
0xaa01, 0x6ac0, 0x6b80, 0xab41, 0x6900, 0xa9c1, 0xa881, 0x6840,
0x7800, 0xb8c1, 0xb981, 0x7940, 0xbb01, 0x7bc0, 0x7a80, 0xba41,
0xbe01, 0x7ec0, 0x7f80, 0xbf41, 0x7d00, 0xbdc1, 0xbc81, 0x7c40,
0xb401, 0x74c0, 0x7580, 0xb541, 0x7700, 0xb7c1, 0xb681, 0x7640,
0x7200, 0xb2c1, 0xb381, 0x7340, 0xb101, 0x71c0, 0x7080, 0xb041,
0x5000, 0x90c1, 0x9181, 0x5140, 0x9301, 0x53c0, 0x5280, 0x9241,
0x9601, 0x56c0, 0x5780, 0x9741, 0x5500, 0x95c1, 0x9481, 0x5440,
0x9c01, 0x5cc0, 0x5d80, 0x9d41, 0x5f00, 0x9fc1, 0x9e81, 0x5e40,
0x5a00, 0x9ac1, 0x9b81, 0x5b40, 0x9901, 0x59c0, 0x5880, 0x9841,
0x8801, 0x48c0, 0x4980, 0x8941, 0x4b00, 0x8bc1, 0x8a81, 0x4a40,
0x4e00, 0x8ec1, 0x8f81, 0x4f40, 0x8d01, 0x4dc0, 0x4c80, 0x8c41,
0x4400, 0x84c1, 0x8581, 0x4540, 0x8701, 0x47c0, 0x4680, 0x8641,
0x8201, 0x42c0, 0x4380, 0x8341, 0x4100, 0x81c1, 0x8081, 0x4040
uint16_t ekmCheckCrc(
const uint8_t const*dat,
uint16_t len
uint16_t crc = 0xffff;
while (len--) {
crc = (crc >> 8) ^ ekmCrcLut[(crc ^ *dat++) & 0xff];
crc = (crc << 8) | (crc >> 8);
crc &= 0x7f7f;
return crc;
ianf
Post by ianf » Fri Jul 06, 2012 1:56 am
Jameson,
Thanks for the information. Do you have a full protocol specification for the meter comms - We need to be able to write configuration to the meters as well as retrieve the time of use and schedule accounting information..
Ian
Post by Jameson » Fri Jul 06, 2012 11:06 am
Hello Ian,
Yes we do have the settings protocol available. It is a bit more challenging to decipher (than our return string parsing sheet), but between it and sniffing the Serial bus while making changes to your meters using the EKM Reader software you should be able to get it.
Here is the command/settings protocol:
http://documents.ekmmetering.com/EKM-Om ... ol_v.3.pdf
With it you should be able to set the meter time, CT Ratios, Reset Maximum Demand, Set Demand Periods, etc
You will also be able to fill in any blanks by using our EKM Reader software. This is best done by using a "serial sniffing" software such as "Advanced Serial Port Monitor". You can then "see" the traffic on the serial bus. And see the command and response structure the meters need to make settings.
ianf
Post by ianf » Fri Jul 06, 2012 12:02 pm
I have a couple of questions and comments after reviewing the V3 meter parsing document.
1. The example shows energy accumulation for 4 transformers. Which meter has a 4th CT input?
2. The Maximum Demand field is 8 bytes, not 7.
3. WRT the date. Capturing network data yields:
0157 3102 3030 3630 2831 3230 3730 3730 3731 3530 3231 3429 034d 63
which translates to the date string: 12070707150214. Is the format YYMMDDWWHHMMSS where YY is year without century, WW is week day with Sunday as the first day of the week?
4, Is Pulse H/L a bitmap of whether the each pulse input is triggered on High or Low level, or is it the current state of the pulse input. If it's the trigger level, how can this be set?
5. Do you have the format of the Seasons and Period tables and the format of the last n month data?
Ian
Post by Jameson » Sat Jul 07, 2012 12:12 pm
Ian,
Thank you for your detailed questions.
ianf wrote: 1. The example shows energy accumulation for 4 transformers. Which meter has a 4th CT input?
EKM-- 1. I think you may be referring to the 4 different time periods the meter returns. The Omnimeter itself keeps track of how many kWh both Total and Reverse have been used in each of 4 time periods. This is for what is called Time-of-Use metering. Some utility customers are charged more for power during the day than at night. In the RS-485 return string you will get these 10 values: Total Kwh, kWh Time Period 1, kWh Time Period 2, kWh Time Period 3, kWh Time Period 4, Reverse kWh (for solar generation back to the grid), Reverse kWh Time Period 1, Reverse kWh Time Period 2, Reverse kWh Time Period 3, Reverse kWh Time Period 4. Let us know if this answers your question.
ianf wrote:2. The Maximum Demand field is 8 bytes, not 7.
EKM-- 2. Thank you very much for catching the typo! The Maximum Demand is 8 bytes in the EKM-Omnimeter return string. We really appreciate the heads up and will update this document.
ianf wrote:3. Is the format YYMMDDWWHHMMSS where YY is year without century, WW is week day with Sunday as the first day of the week?
EKM-- 3. Yes you have it correct. YY is the year without the century, and WW in the day of the week (starting on Sunday). If WW = 04 this would be Wednesday. YY=year MM=month DD=day WW=day of week HH =hour MM=minute SS=second
ianf wrote:4, Is Pulse H/L a bitmap of whether the each pulse input is triggered on High or Low level, or is it the current state of the pulse input. If it's the trigger level, how can this be set?
EKM-- 4. The Pulse section of this document is for a yet to be released pulse counting EKM-Omnimeter. And yes the H/L portion is an indication of if the pin is pulled High or Low at the given moment (or as you say the current state of the 3 pulse input pins).
ianf
Post by ianf » Sat Jul 07, 2012 2:16 pm
Jameson wrote: EKM-- 1. I think you may be referring to the 4 different time periods the meter returns. The Omnimeter itself keeps track of how many kWh both Total and Reverse have been used in each of 4 time periods.
Ah, silly me. I was thinking phases, not ToU.
Ian
tarannar
Post by tarannar » Fri Jul 27, 2012 2:55 pm
I clicked the link for the settings protocol above (http://documents.ekmmetering.com/Meter_ ... rt_v.3.pdf) and I get returned the same document for the meter data response string. Tried a couple of different web browsers to make sure it wasn't my issue.
Most importantly, I'm trying to determine if there is a way I can query the RS-485 bus to determine the meter ID's on the line. I currently have software which has the meter ID hardcoded for communications and I'd like to make it smarter.